Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Part load ratio performance coefficients for chiller and unitary DX system

asked 2020-04-24 01:58:26 -0600

VS's avatar

updated 2020-04-24 08:20:30 -0600

I am trying to calculate part load ratio performance coefficients for water cooled chiller and unitary system. For Water cooled chiller, EIRfPLR curve coefficients can be get from Energy Plus curve fit tool(excel sheet) in quadratic form? And for unitary DX system, Part load fraction correlation curve was available in Energy Plus - Engineering Reference document (pg no. 818) PLR=0.85+0.15(PLR), can I use this same correlation values for simulation?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2020-04-24 12:53:31 -0600

The DX coil part load fraction correlation curve PLR=0.85+0.15(PLR) should be used for simulation.The 0.85 in this correlation represents high efficiency DX equipment. Low efficiency DX equipment would use 0.75 to 0.80 (but I have no reference for this).

edit flag offensive delete link more

Comments

Thank you for your answer. Any idea about EIRfPLR (Energy Input Ratio function of Part load Ratio) curve coefficients for water cooled chiller. Whether that can obtained from Energy Plus curve fit tool excel by using quadratic form. Are any other way to find this coefficients?

VS's avatar VS  ( 2020-04-25 06:48:25 -0600 )edit

Yes the tool can be used for water-cooled chillers. Just input water temps instead of air temps.

rraustad's avatar rraustad  ( 2020-04-27 05:45:21 -0600 )edit
1

In order to calculate EIR as a function of PLR, you wouldn't you need to have PLR (Flow Fraction) as the independent variable? And further, to control for temperature on a quadratic curve, wouldn't the temperatures (Evaporator and Condenser Entering Temperatures) have to be held constant for the range of data?

Ski90Moo's avatar Ski90Moo  ( 2020-05-20 13:00:51 -0600 )edit
1

The chiller EIRfPLR can't be calculated using the CurveFitTool provided with E+. But it's really only a power fraction curve that roughly goes from 0 at PLR=0 to 1 at PLR=1. I did say "roughly" so bear in mind there is a little bit of a bend to this curve. Plot a chiller curve and you will see.

rraustad's avatar rraustad  ( 2020-05-20 15:34:34 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2020-04-24 01:58:26 -0600

Seen: 792 times

Last updated: Apr 24 '20