Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Heatrecovery - Not working

asked 2020-04-06 22:06:52 -0500

updated 2020-04-07 17:44:57 -0500

Currently, within my model, no heat recovery value is being registered when I run my model within the 'End Uses' table in the Results Summary (I can not currently upload any images).

Energy recovery ventilation (ERV) I am using HeatExchanger:AirToAir:SensibleAndLatent to model the heat recovery within my VAV system

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2020-04-07 16:31:11 -0500

updated 2020-04-07 16:31:38 -0500

Only the enthalpy wheel motor is included under heat recovery if you set the type to 'enthalpywheel' in the HeatExchanger:AirToAir:SensibleAndLatent object. Otherwise, all energy in your ERV is from the supply and exhaust fans which are included under the Fans end use. You can set an energy use subcategory on these fans to split out which ones are in ERVs vs. others in the building.

edit flag offensive delete link more

Comments

Thanks for your help!

Rachel-New Zealand's avatar Rachel-New Zealand  ( 2020-04-13 02:02:45 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2020-04-06 22:06:52 -0500

Seen: 139 times

Last updated: Apr 07 '20