Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Material Emissivity - EnergyPlus

asked 2020-04-03 04:16:31 -0500

NCB's avatar

updated 2020-08-19 10:17:40 -0500

I'm trying to modelate a cool roof, but i'm not completely secure that the emissivity of the material it is contemplated in the material properties of EnergyPlus. I'm mistaken? What is the best way to define a cool-roof?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2020-04-03 12:02:06 -0500

When EnergyPlus performs the heat balance for the outside face of a surface, it assumes that the emissivity is equal to the absorptance. Since the roof is opaque, transmittance is zero, making reflectance = (1 - absorptance).

$$ \alpha = \epsilon$$ $$ \tau = 0$$ $$ \rho = 1- \alpha$$

If you're modeling a cool roof that has high reflectance, you will want to set the absorptance input fields in EnergyPlus to low values. You can read more information in this post and this post.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2020-04-03 04:16:31 -0500

Seen: 662 times

Last updated: Apr 03 '20