Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

District heating in EnergyPlus

asked 2020-03-25 10:42:30 -0500

chrisis's avatar

updated 2020-03-25 17:26:59 -0500

Hi there! I am facing the problem on how to model a district heating by using e+. Could I ask you which type of components do I have to use in Eplus launch? A simple case it would be ok- Thanks agian for the help!! Christian

edit retag flag offensive close merge delete

Comments

1

I started to take a look at WindACAirtoAir.idf . Sometimes I get lost because there are several components. By the way, I cannot understand the component named Sizing zone. In such component are specified the supply air temperature for cooling 12 and heating 50 when the temperature setpoints in the schedule compact are different for both heating and cooling. Moreover, do you know a convenient way to make a skatch of the building envelope in some free cad program in order to import the drawing into WindACAirtoAir.idf file?

chrisis's avatar chrisis  ( 2020-03-29 16:20:39 -0500 )edit

@chrisis this is really a different question and should be created as a new post. However, there is already a post that discusses the Sizing:Zone object, as well as another post that discusses tools to visualize and edit the geometry of EnergyPlus files. Please search existing posts on Unmet Hours to try and answer your question before adding a new post.

Aaron Boranian's avatar Aaron Boranian  ( 2020-03-30 08:53:03 -0500 )edit

Thanks again Aaron and sorry for the mess

chrisis's avatar chrisis  ( 2020-03-30 12:46:29 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
1

answered 2020-03-26 03:54:39 -0500

updated 2020-03-26 05:51:43 -0500

Hi,

you have to connect your hot water loop to the District Heating object as hot water generator (Primary Supply Side), than to as many Fluid-to-fluid heat exchangers as you need on Primary Demand Side to model the heat exchanger substation at building level.

These Fluid-to-fluid heat exchangers will be on the Secondary Supply Side, than finally the you have to put the teminal units yuo need (radiators, fan coil units, AHU coils,....) to the Secondary Demand Side.

Obviously every loop (the Primary and the Nth Secondary) need to have their own pumps in order to move hot water flows and be properly controlled.

Ag

edit flag offensive delete link more

Comments

Hi, thanks again for your answer. I will try in the next days and then I will let you know. Best regards, Christian

chrisis's avatar chrisis  ( 2020-03-26 05:48:06 -0500 )edit

It is also possible to put the terminal units, radiators, coils, etc. on the primary demand side. You don't necessarily have to use water-to-water heat exchangers to "bridge" heat transfer from district heating/cooling to these types of HVAC components. Check out the EnergyPlus example file WindACAirtoAir.idf to see an example of one Hot Water Loop with district heating on the supply side and hot water baseboards on the demand side.

Aaron Boranian's avatar Aaron Boranian  ( 2020-03-26 08:54:55 -0500 )edit

Yes, for sure you're right. I was supposing for a district heating serving multiple buildings, that is a District Heating as in the topic, and not just a single building served by a District Heating

Ag's avatar Ag  ( 2020-03-26 11:00:38 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

Stats

Asked: 2020-03-25 10:41:32 -0500

Seen: 715 times

Last updated: Mar 29 '20