Not to run a program if there is no inputs in the model, CO2 Control
Hello Everyone,
I'm writing a script to control CO2 concentration through natural ventilation. There are different kind of spaces with different levels of CO2 allowed, which I want to use in all my projects. That’s why I need the script to have all the options, but not to run the options that are not in the model. The thing is that when I run a model with spaces that are not defined in the EMS, the following error occurs:
** Severe ** IP: IDF line~5428 Error detected in Object=ENERGYMANAGEMENTSYSTEM:PROGRAM, name=CO2WINDOWCONTROLIDA1
** ~~~ ** Field [Program Line 1] is required but was blank
** Severe ** IP: Blank "required" fields found in input
** Severe ** IP: Out of "range" values and/or blank required fields found in input
** Fatal ** IP: Errors occurred on processing IDF file. Preceding condition(s) cause termination.
The script I Used i that:
! SENSOR IDA1
<ForAllWindows> {ZoneIDFName=IDA1;Tag=CO2}
EnergyManagementSystem:Sensor,
<LoopWindowVariableName>Air_CO2_Concentration_IDA1,
<LoopWindowZoneIDFName>,
Zone Air CO2 Concentration;
! ACTUADOR IDA1
EnergyManagementSystem:Actuator,
Venting_Opening_Factor_IDA1<LoopWindowVariableName>,
<LoopWindowIDFName>,
AirFlow Network Window/Door Opening,
Venting Opening Factor;
<LoopNextWindow>
! extra outputs for viewing in the results viewer
<If BuildingAttribute HourlyOutput = 1 Then>
Output:Variable, *, Zone Air CO2 Concentration, hourly;
<Endif>
<If BuildingAttribute TimesteplyOutput = 1 Then>
Output:Variable, *, Zone Air CO2 Concentration, timestep;
<Endif>
! NAME IDA1 PROGRAM
EnergyManagementSystem:ProgramCallingManager,
CO2 Window Control IDA1,
InsideHVACSystemIterationLoop,
CO2WindowControlIDA1;
! programa per a IDA1
EnergyManagementSystem:Program,
CO2WindowControlIDA1,
<ForAllWindows> {ZoneIDFName=IDA1;Tag=CO2}
If <LoopWindowVariableName>Air_CO2_Concentration_IDA1 <> Null,
! Proportional control of window opening
! CO2 levels in zone for this window
SET ZoneCO2 = <LoopWindowVariableName>Air_CO2_Concentration_IDA1,
! CO2 level giving rise to lowest opening factor
SET ZoneCO2Min = 650,
! Lowest opening factor
SET OpenFactZoneCO2Min = 0,
! CO2 level giving rise to highest opening factor
SET ZoneCO2Max = 750,
! Highest opening factor
SET OpenFactZoneCO2Max = 0.1,
IF ZoneCO2 <= ZoneCO2Min,
SET OpenFact = OpenFactZoneCO2Min,
ELSEIF ZoneCO2 >= ZoneCO2Max,
SET OpenFact = OpenFactZoneCO2Max,
ELSE,
SET m = (OpenFactZoneCO2Max - OpenFactZoneCO2Min) / (ZoneCO2Max - ZoneCO2Min),
SET C = (OpenFactZoneCO2Min + OpenFactZoneCO2Max - m * (ZoneCO2Min + ZoneCO2Max)) / 2,
SET OpenFact = m * ZoneCO2 + C,
ENDIF,
SET Venting_Opening_Factor_IDA1<LoopWindowVariableName> = OpenFact,
<LoopNextWindow>
<ENDIF>
;
I used If <LoopWindowVariableName>Air_CO2_Concentration_IDA1 <> Null,
before running the program but seems it didn't work,
Any help wouyld be great,
Thank you!
IDF in the link https://www.dropbox.com/s/vt9xwviqnrh...