Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Change Outdoor Air specification per zone in openstudio

asked 2020-03-12 23:23:55 -0500

How can I specify individual Outdoor Air flows per zone in openstudio? Right now i have repeating specifications and if I try to change the value for individual zones I end up changing several spaces. I need this for compliance with ASHRAE 90.1-2007.The model is here

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2020-03-13 12:36:08 -0500

Design Specification Ventilation Design Flow Rate objects are a shared resource, but it is confusing, because unlike other shared resources, it doesn't show up in the internal load tab (like people, lights, etc).

The easiest way to make a unique instance is to drag on in from the library to the space or space type you want to change. Then You will have a unique rescue that you can rename and change characteristics for. For reference infiltration objects have similar but not exactly the same behavior.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2020-03-12 23:23:55 -0500

Seen: 87 times

Last updated: Mar 13 '20