Change Outdoor Air specification per zone in openstudio

asked 2020-03-12 23:23:55 -0600

How can I specify individual Outdoor Air flows per zone in openstudio? Right now i have repeating specifications and if I try to change the value for individual zones I end up changing several spaces. I need this for compliance with ASHRAE 90.1-2007.The model is here

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2020-03-13 12:36:08 -0600

Design Specification Ventilation Design Flow Rate objects are a shared resource, but it is confusing, because unlike other shared resources, it doesn't show up in the internal load tab (like people, lights, etc).

The easiest way to make a unique instance is to drag on in from the library to the space or space type you want to change. Then You will have a unique rescue that you can rename and change characteristics for. For reference infiltration objects have similar but not exactly the same behavior.

edit flag offensive delete link more