Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Discrepancy in values in running both Conventional and VRF systems in 2 different locations.

asked 2020-03-09 12:26:25 -0500

bmjohn's avatar

updated 2020-03-11 08:04:37 -0500

I have run a model using VRF and conventional systems in 2 different locations from CBECC and OpenStudio. The Design Size Gross Rated Total Capacity happens to be the same for both VRF and Conventional but is different for another location. I am not sure why that difference occurs. Does anyone have any pointers? I will appreciate it.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2020-03-11 07:33:31 -0500

updated 2020-03-12 19:45:42 -0500

When autosizing components the simulation uses the weather data to determine the conditions used for sizing. This includes the zone load and coil inlet condition. I would expect the coil size to change with location. The amount of outdoor air will also impact coil sizing where zone and air loop equipment size OA quantities differently. You can review the eio file to see the zone loads and the html file shows the coil and outdoor air sizing details.

edit flag offensive delete link more

Comments

Thank you, Richard, for sharing that information. I have had the opportunity to read some of your papers for FSEC.

If the above is true, I would assume that the "Design Size Gross Rated Total Capacity" should be different for all locations? In my case I found one location having the same "Design Size Gross Rated Total Capacity" for both VRF and Conventional systems, but when the location changed there was a drastic difference between VRF and Conventional system?

bmjohn's avatar bmjohn  ( 2020-03-11 11:49:07 -0500 )edit
1

Another difference is the performance curves used for each coil model. The CapFT curve is used during sizing to adjust coil size after the size is selected. For example, if the CapFT result at the cooling coil inlet WB and outdoor temperature used for sizing = 1.1, then the coil size is reduced 10%. I assume you are not using the same coil performance curves and therefore the coil size for a specific location could be different.

rraustad's avatar rraustad  ( 2020-03-11 11:56:39 -0500 )edit

That does make sense, But in my case, I have used the same performance curves (FSEC) and still found the total capacity value to be different.

bmjohn's avatar bmjohn  ( 2020-03-11 14:14:23 -0500 )edit

What other system are you using. I may need the inputs files to decipher this further.

rraustad's avatar rraustad  ( 2020-03-11 14:35:35 -0500 )edit

I misunderstood your statement about the performance curves. Yes, you are right, the model uses different performance curves for VRF and Conventional systems. However, I am not yet sure why one of the locations the VRF and conventional models gave the same values for "Design Size Gross Rated Total Capacity" whereas the other locations shown a drastic difference in the values. I could share the CBECC-Com project files for the locations. Is there an email to which I can forward it to? Thanks!

bmjohn's avatar bmjohn  ( 2020-03-12 09:24:29 -0500 )edit

I just need the 4 idf files. 2 for one location, 2 for the other. email is in profile. I might not get to this until next week.

rraustad's avatar rraustad  ( 2020-03-12 09:52:27 -0500 )edit

Did you not see these errors, in the err file? Something is wrong with your performance curves.

** Warning ** GetDXCoils: Coil:Cooling:DX:VariableRefrigerantFlow="COILCOOLING 11" curve values
**   ~~~   ** ... Cooling Capacity Ratio Modifier Function of Temperature Curve Name = COILCLGVRFCLGQRATIO_FTWBTDBSI output is not equal to 1.0 (+ or - 10%) at rated conditions.
**   ~~~   ** ... Curve output at rated conditions = 15.000
rraustad's avatar rraustad  ( 2020-03-12 13:35:33 -0500 )edit

Well I just checked and that performance curve doesn't give 15 at rated conditions. Something else is going on.

rraustad's avatar rraustad  ( 2020-03-12 13:52:22 -0500 )edit

Since I was reading the values of CBECC-Com, I did not run into the error file. All of the curves within the model are the default coefficients itself as well.

bmjohn's avatar bmjohn  ( 2020-03-12 14:02:16 -0500 )edit
1

From a review of the 2 files I see differences between the amount of outdoor air the DX coils see and are therefore sized with. The air loops have mechanical ventilation controllers and use OA specs of 0.000762 m3/m2 of OA per floor area (results in about 20% OA). The VRF system will autosize the OA flow rate to be the maximum of the cooling or heating flow rates (results in 100% OA).So without actually comparing the results I suspect the VRF coils are larger than the conventional coils.

rraustad's avatar rraustad  ( 2020-03-12 14:20:54 -0500 )edit
1

The perf curve coeffs look good but min curve output = 15 and max curve output = 23.89 and min WB (x) = 20. These need fixing.

Curve:Biquadratic,
  CoilClgVRFClgQratio_fTwbTdbSI,  !- Name
  0.058588,  !- Coefficient1
  0.05874,  !- Coefficient2 x
  -0.00021,  !- Coefficient3 x**2
  0.010937,  !- Coefficient4 y
  -0.000122,  !- Coefficient5 y**2
  -0.000525,  !- Coefficient6 x*y
20,  !- Min Value of x
  43.33,  !- Max Value of x
  0,      !- Min Value of y
  100,   !- Max Value of y
15,     !- Min Curve Output
23.89;  !- Max Curve Output
rraustad's avatar rraustad  ( 2020-03-12 14:54:21 -0500 )edit

Make sure you check all the curves since I only highlighted problems with 1 curve.

rraustad's avatar rraustad  ( 2020-03-12 14:55:41 -0500 )edit

Thanks Richard! I will look into them. I believe this resolves my issue. Thanks a lot!

bmjohn's avatar bmjohn  ( 2020-03-12 19:35:45 -0500 )edit

Responding to this comment: The perf curve coeffs look good but min curve output = 15 and max curve output = 23.89 and min WB (x) = 20. These need fixing.

Having looked into that, it seems those values are present within the idf files generated by CBECC-Com. So should the CBECC-Com not update them automatically?

bmjohn's avatar bmjohn  ( 2020-03-16 16:47:00 -0500 )edit

Responding to comment:
From a review of the 2 files I see differences between the amount of outdoor air the DX coils see and are therefore sized with. The air loops have mechanical ventilation controllers and use OA specs of 0.000762 m3/m2 of OA per floor area (results in about 20% OA)....

I have manually changed the OA specs for VRF to m3/m2, did not cause any change in the cooling/ heating/ fan loads either. Is that of concern?

bmjohn's avatar bmjohn  ( 2020-03-16 16:51:42 -0500 )edit

Funny coincidence, I found this very same issue in the CBECC-Com curves two weeks ago. I've created a ticket for the development team to address this in our next release. Not sure how this error did not get noticed sooner. after I fixed it locally, I did not see a dramatic change in energy use. @bmjohn, after fixing the min/max curve outputs, did you see a big change in energy use?

DavidReddy's avatar DavidReddy  ( 2020-03-17 00:51:08 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

Stats

Asked: 2020-03-09 12:26:25 -0500

Seen: 154 times

Last updated: Mar 12 '20