How to implement centralized ventilation system without heating or cooling in energyplus idf editor?

asked 2020-03-08 10:32:58 -0500

Ben_M's avatar

Hi all, For our master thesis project i want to implement a centralized ventilation system to a school building with different zones, which is seperate from the existing heating system (baseboard heating).

We tried it with the "HVACTemplate:System:UnitarySystem" object (without heating and cooling coils) and an "HVACTemplate:Zone:Unitary" object for each zone with the first object assigned as the Template Unitary System.

Since there is already a I"HVACTemplate:Zone:BaseboardHeat" object used for heating in all existing zones, we get following severe error for each zone (e.g. the music class) and the simulation does not work:

* Severe * Duplicate name found. name: "Music class (100) Equipment". Overwriting existing object.

We are thankful for any suggestions regarding this problem. Kindly find attached our file and thanks in advance!

edit retag flag offensive close merge delete

3 Answers

Sort by ยป oldest newest most voted
0

answered 2020-11-27 04:10:04 -0500

Adrien's avatar

Since HVACTemplate:Zone:Unitary has some fields named "Baseboard Heating...", I think that it can do the same as HVACTemplate:Zone:BaseboardHeat and more, and I guess that you can safely delete the HVACTemplate:Zone:BaseboardHeat objects after having reported their configurations to your HVACTemplate:Zone:Unitary objects... can someone with experience please confirm?

edit flag offensive delete link more
0

answered 2020-11-27 06:25:13 -0500

updated 2020-11-27 06:25:28 -0500

There is no reasons to get a Severe Error if the same name is applied to different Object Type. The error must be elsewhere.

You should go through the IDF, objects name, but I do not find any attached file

edit flag offensive delete link more

Comments

I confirm that the HVAC templates expansions will lead to the above mentioned errors when HVACTemplate:Zone:BaseboardHeat and HVACTemplate:Zone:Unitary are defined simultaneously for the same zone because two different ZoneHVAC:EquipmentList with the same name will be generated (one for each HVAC template object). I guess that this is OK though because the templates are not supposed to cover complex cases...

Adrien's avatar Adrien  ( 2020-11-30 09:43:19 -0500 )edit

@Adrien, thank you for having shared your deeper analysis

Ag's avatar Ag  ( 2020-12-01 03:45:13 -0500 )edit
0

answered 2020-11-27 20:40:40 -0500

This is going to be the long way to get there, but it seems like it would benefit you..

If it were me, I'd download and install CBECC-Com which is a free software interface for doing code compliance in California. However, it runs on the EnergyPlus engine and installs with sample files, including two with DOAS systems (dedicated outdoor air system ==> aka centralized ventilation systems). Open one of the sample models such as Documents\CBECC-Com 2019.1.3 SP1 Projects\OtherTests2019\RetlSml-DOAS+FPFC19.cibd19, run it, and then find the IDF file for the proposed file in the project directory.. This will give you an idea of how a system would actually be set up, and you can modify from there.

edit flag offensive delete link more