First time here? Check out the Help page!

Sorry, this content is no longer available

Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Can I model a tank which has three different inputs and outputs?

asked 5 years ago

mayks's avatar

updated 5 years ago

Hello, I´m modelling a system in energyplus that has three cooling towers and three chillers and all of them are coupled to one accummulation tank. What object can I use? (I tried to use ThermalStorage:ChilledWater: Mixed but I just can put one inlet and one outlet node). The inlets of the accumulation tank comes from the cooling towers and then goes to the chiller.

I also want to know which object can I use for a stratified tank that can have also three inlets. Thank you

Preview: (hide)

2 Answers

Sort by » oldest newest most voted
1

answered 5 years ago

mayks's avatar

I see what you have done, but my system is composed by two differnt loops each one with a different coolingTower and chiller but ther are connected through the tank. Can I still do it as you? My system is in the link below

link text

Preview: (hide)
link

Comments

This should have been a comment and not an answer. I'm getting a 403 (forbidden access) at the link you gave.

Julien Marrec's avatar Julien Marrec  ( 5 years ago )
mayks's avatar mayks  ( 5 years ago )
1

answered 5 years ago

I can suggest an idea...

Your Cooling Towers would be on the supply side of a plant loop, on parallel branches. Then it mixes via the PlantLoop Mixer, goes to the demand side, at which point you just place a WaterHeater:Mixed (or WaterHeater:Stratified).

That WaterHeater:Mixed is then on the supply side of another plant loop, and on the demand side you place all three chillers in parallel (their condenser nodes). The Pump for that loop can be "virtual" with a very low pressure rise and almost 0 power used.

The three chillers are then on the supply side of the Chilled water loop (evaporator side), serving the building load.

Here's a showcase of my Pinta (Paint) skills:

image description


An alternative may be to use just two loops and to manually set a large Plant Loop Volume for the PlantLoop "condenser water loop".

Preview: (hide)
link

Comments

Is the Cooling Tower operation controlled by the temperature of the tank? (with a bypass not shown?)

Julien Marrec's avatar Julien Marrec  ( 5 years ago )

yes the cooling tower is controlled by the tank I didn´t draw the bypass pipes, but they all have

mayks's avatar mayks  ( 5 years ago )

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 5 years ago

Seen: 265 times

Last updated: Feb 20 '20