Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

Trane Trace Energy Modeling Ventilation OA hourly amount

asked 2020-02-12 15:51:15 -0500

KLim's avatar

updated 2020-02-12 17:25:47 -0500

Hi. I am working on energy modeling with Trane Trace 700, so I have proposed model and baseline model. Based on the code, I am using the minimum OA for thermal zones in both models with same amount. However, the result from Trane Trace shows me different outdoor air amount in hourly. The total amount of OA is same in Airflow report however, in hour Ventilation chart shows me dramatic difference between baseline model and proposed model. How that hourly OA amount is calculated? Is that space peak? or coil peak?

Thank you.

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
3

answered 2020-02-12 21:03:26 -0500

tj.olson's avatar

Hi KLim, I would suggest you contact CDS support.

cdshelp@trane.com 608-787-3926

Since you are speaking of a specific project file you are working on it would be useful to send in the archived (.taf) file attached in your email so we can understand your question better. Also if you have screen shots showing the differences in your reports that would also be helpful.

edit flag offensive delete link more

Comments

1

Hello, I am not sure if you were able to contact CDS support. If you haven't I would still recommend you reach out so they can look into your question at a deeper level. In TRACE 700 the VRF system is allowed to modulate down to 10% airflow for low load operation. PTHP systems are constant volume only. This more than likely explains the large difference in cfm between the two. However, to answer the question with more confidence it would be best to see your file. That way the ventilation schedules and any ventilation settings at the system level can be reviewed.

tj.olson's avatar tj.olson  ( 2020-02-18 08:46:44 -0500 )edit
1

answered 2020-02-13 07:53:49 -0500

updated 2020-02-13 07:55:20 -0500

Since OA is controlled based on HVAC operation, it might be that the OA differs because the air loop operation is different (e.g., building loads are different). You should also include information about the type of HVAC system to better understand possible reasons for the difference you see.

edit flag offensive delete link more

Comments

Hi. Thank you for answering. The project is about residential building and proposed model has VRF system for residenatial area. In baseline model, obviously having PTHP. The loads for both model are different based on different construction set. I believe HVAC system operates based on the setpoints in the model and ventilation schedule. But still do not get why different amount of outdoor air hourly.

KLim's avatar KLim  ( 2020-02-13 10:17:19 -0500 )edit
1

Does baseline PTHP use constant fan mode or cycling fan mode?

rraustad's avatar rraustad  ( 2020-02-13 10:57:52 -0500 )edit

Hi. It was constant fan mode as given in Trane Trace followed by ASHRAE 90.1

KLim's avatar KLim  ( 2020-02-13 11:09:20 -0500 )edit
1

Can you compare the hourly supply air flow?

rraustad's avatar rraustad  ( 2020-02-13 11:17:44 -0500 )edit

The main cooling and heating coils for both model, main heating coil airflows are same for both model but having huge difference in cooling

KLim's avatar KLim  ( 2020-02-13 11:28:19 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2020-02-12 15:51:15 -0500

Seen: 459 times

Last updated: Feb 13 '20