Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Is the Chilled water cooling coil total load same as the chiller capacity?

asked 2020-02-03 23:05:03 -0600

Prasanth M's avatar

updated 2020-02-08 12:01:31 -0600

Hi group, I am new to EnergyPlus, is chiller capacity same as the chilled water cooling coil total load?

Please clear my doubt.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2020-02-04 07:29:36 -0600

The report variable Cooling Coil Total Cooling Rate is actually the air-side total cooling rate and should be equal to the water-side load on the plant imposed by the water coil. You can test this by calculating the water-side energy rate using the mass flow rate of the water coil outlet node (using the report variable System Node Mass Flow Rate) and multiplying by the water-side enthalpy difference between water coil inlet and outlet node ( difference of System Node Enthalpy at water coil inlet and outlet). This load is passed to the plant and is added to any pump heat or piping losses (may be 0 if not modeled) to equal the total chiller load (Chiller Evaporator Cooling Rate).

edit flag offensive delete link more

Comments

Thank you Mr.Richard Raustad for clearing my doubt.

Prasanth M's avatar Prasanth M  ( 2020-02-05 00:54:49 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2020-02-03 23:05:03 -0600

Seen: 493 times

Last updated: Dec 23 '20