Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Kiva error simulation EnergyPlus

asked 2020-02-03 04:54:40 -0500

NCB's avatar

updated 2020-02-03 07:08:14 -0500

I'm trying to simulate Kiva with EnergyPlus, but the next error continues to come out.

 ** Severe  ** Foundation:Kiva="<Default Foundation>", only one floor per Foundation:Kiva Object allowed.

What this is mean? Im quite new in simulation with EnergyPLus and Kiva but i need to calculate the ground surface temperature. Somebody can help me?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2020-02-03 09:41:28 -0500

Please view the E+ documentation for the Kiva:Foundation object. Specifically note where it talks about limitations and says

Exactly one floor surface must reference each Foundation:Kiva object. However, multiple floors may exist in the same thermal zone so long as they reference separate Foundation:Kiva objects.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2020-02-03 04:54:40 -0500

Seen: 115 times

Last updated: Feb 03 '20