Modeling VRF without exhaust node

asked 2020-01-22 00:45:46 -0600

sinocap's avatar

updated 2020-01-22 19:59:46 -0600

Hi. all.

I am making the VRF model which 1-way cassette using energy plus.

In this system, the outside air is supplied to the room pass through a cooling and heating coil(This is the same as the existing VRF example in the Energy Plus).

In all existing example model, there must be an exhaust node in ZoneHVAC:EquipmentConnections.

However, I want to make a model without exhaust node, because the actual VRF system uses only outside air and not indoor air.

In other words, the actual VRF system only supplies cool or hot air to the room, but it does not suck indoor air. Is it possible? Thank you.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
0

answered 2020-01-22 09:15:45 -0600

Not at this time. However, E+ is adding the ability for VRF to be used in an air loop and that will solve this problem. Hopefully this will be included in the next release. See pull request 7605.

edit flag offensive delete link more

Comments

Thank you for your reply! I wish this will be update in next version.

sinocap's avatar sinocap  ( 2020-01-27 22:51:01 -0600 )edit