Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

Performance curves in HVAC templates in Energyplus

asked 2020-01-18 06:34:12 -0600

Rshree's avatar

updated 2020-01-18 10:02:50 -0600

Where is the information regarding what type of performance curves are used when we model HVAC using HVAC templates in Energy plus?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2020-01-19 04:59:55 -0600

Jim Dirkes's avatar

Going from memory.... The type of curve depends on the E+ object that's in use. You may know that when you run a template, the IDF file gets expanded into a complete, non-template IDF. Find out which objects are created in that new IDF and use curves of interest to you. Next, search the Input Output Reference which is included in the E+ documentation for the object of interest and it will tell you which curve type are acceptable

edit flag offensive delete link more

Comments

1

As a note, the "complete, non-template IDF" that Jim refers to ends in [file_name].expidf (short for "expanded IDF") instead of [file_name].idf (file that defines HVAC templates). This expanded IDF is created by the pre-processor tool named ExpandObjects, which can be used stand-alone before running a simulation or after you run a simulation with EP-Luanch by default.

Aaron Boranian's avatar Aaron Boranian  ( 2020-01-19 12:05:09 -0600 )edit

Thank you for such clear replies. It is very helpful.

Rshree's avatar Rshree  ( 2020-01-22 10:09:24 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2020-01-18 06:34:12 -0600

Seen: 225 times

Last updated: Jan 19 '20