How to fix the not met hours?
I am almost new to EnergyPlus, I tried to build a model by merging the geometry of the reference small office building and the ventilation system of a reference large office building. Furthermore, I selected the "autosize" option for determining the nominal capacity of the reheat coils in the terminal boxes, but I get "0" [W] capacities for all the reheat coils when I run the simulation on the whole weather file. Such a problem leads to a significant number of not met hours of heating periods. (I just joined the website and do not have enough credits to attach the model.)
The idf. text file: https://justpaste.it/4lkhp
This is not enough information to identify the problem. Do you have thermostats in all controlled zones? Does the err file show any details that may help the diagnosis? What is the location? What is the zone temps in winter and summer (just one zone will suffice)?
The original question has updated with a idf. text file of the model. The office building is located in Chicago with 5 zones equipped with "ThermostatSetpoint:DualSetpoints" follow the existing CLG and HTG setpoints. The temperature change of each zone has the following range: - CORE_ZN: 9.7 - 27 [C] - Perimeter_ZN: 7.0 - 27 [C]
Regarding the final errors, there is no fatal or sever errors. But the following errors are recorded: 1. Pump nominal power or motor efficiency is set to 0. 2. The condenser outlet temperature is outside the range of cond. outlet temp