Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Ideal Load Air System

asked 2019-12-11 09:57:01 -0500

arnespandau's avatar

Hello Users, I use IDF Editor for my building. I want to add an ZoneHVAC:IdealLoadAirSystem to one of the zones. This system is just for heating. The set temperature in the zone is 21°C. If the outside temperature is over 15°C the heater is off. I know how I have to define the schedules for the set temperature but what is the easiest way to add the shut down temperature of 15°C? Regards, Arne

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
3

answered 2019-12-11 10:38:30 -0500

One option is to create an EMS program that actuates the Availability Schedule of the ideal air system. The EMS program should use a calling point that occurs early in the zone timestep, and would set the availability schedule to off or on based on the outdoor drybulb temperature (retrieved via an EMS sensor).

edit flag offensive delete link more

Comments

Thanks for your answer! But is there a way to do that in the IDF Editor, without creating a program?

arnespandau's avatar arnespandau  ( 2019-12-11 10:53:34 -0500 )edit
1

You could pre-process the weather file, find the hours where outside temperature is above 15C, and create a detailed ideal system availability schedule to reflect that.

shorowit's avatar shorowit  ( 2019-12-11 11:00:26 -0500 )edit

Okay I thought there is maybe a easier way with less work.

arnespandau's avatar arnespandau  ( 2019-12-11 11:03:50 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

2 followers

Stats

Asked: 2019-12-11 09:57:01 -0500

Seen: 333 times

Last updated: Dec 11 '19