Transcritical compressor coefficients

asked 10 years ago

updated 9 years ago

Has anyone been successful obtaining and using manufacturer compressor curves for transcritical CO2 refrigeration systems? I have attempted to download the transcritical/subcritical compressor curves from manufacturer and apply in model; however, the energy use is all over the place (extremely negative OR extremely positive).

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
3

answered 10 years ago

EnergyPlus doesn't follow the ARI Standard 540 exactly and requires the user to tweak the order of the coefficients for compressor performance curves. Also make sure your coefficients are in the right units where applicable.

Preview: (hide)
link

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.