ventilation - infiltration

asked 2019-11-10 11:21:37 -0500

luperuch's avatar

Hi, I am performing a simulation in Design builder, with a set value of infiltrations and a mechanical ventilation for the IAQ requirement. I would like to configure that the contribution of mechanical ventilation is complementary to infiltrations. In other words, for example, if I have 0.5ach infiltration and I require 0.65ach for IAQ, I want that the mechanical ventilation provides 0.15ach. I don't know if this is possible to configure, the results I am having is the sum of the infiltration rate plus the ventilation rate. (example: 0.5 + 0.65 ach) Thanks in advance!

edit retag flag offensive close merge delete

Comments

I don't believe EnergyPlus will do this for you. You will have to schedule infiltration and ventilation amounts yourself. Nevertheless, how can you know that infiltration will provide 0.5 1/h of outdoor air reliably?

lisang's avatar lisang  ( 2020-03-10 08:39:18 -0500 )edit