How can I define openable window (half open) in Energy+?

asked 2019-10-11 08:06:10 -0600

kaca's avatar

updated 2019-10-15 05:36:57 -0600

Hi i want define openable window in energy+, i use tool Zone:Ventilation:WindandStackOpenArea. Before I created new schedule for night ventilation, which was used in Zone:Ventilation:WindandStackOpenArea. When I get outputs i have problem with ari change rate, the value are 45 ach. Where i made mistake? It is nessesary set something else? I tried change opening area from 1,7m2 to 0,455m2 but air change rate was still 45ach, what is strange for me. Thank you image description

edit retag flag offensive close merge delete

Comments

Can you paste your ZoneVentilation:WindandStackOpenArea object so we can look at what you put in it?

Julien Marrec's avatar Julien Marrec  ( 2019-10-15 05:37:58 -0600 )edit

Hi, i used this setting: opening area: 1,72m2 (high: 1,15m width: 1,5m), opening effectivness: autocalculate, effective angle: 127 (east), height difference: 1m, discharge coeffficient for opening: autocalculate. Then air change rate is 89,7 ach, volume of my zone is 47m3. I didn't set temperature and wind speed limits, i want investigative what happened when window is open during night (i setted schedule for window openable). I checked weather data- wind speed was around 3 m/s. Also I want ask you if it possible set with this tool se angle for ventilation of window (for example 10°) Thanks

kaca's avatar kaca  ( 2019-10-15 06:06:09 -0600 )edit

Paste the snippet please, the actual IDF object. It'b be more readable. You can edit your question and paste it inside a code block (4 space indentation, or click the 0101 button)

Julien Marrec's avatar Julien Marrec  ( 2019-10-15 15:20:43 -0600 )edit