Heating cooling demand and district systems

asked 2019-07-18 04:54:49 -0500

gonchotorena's avatar

updated 2019-07-18 11:23:15 -0500

I haventaven't got a clear idea of district heating and cooling. Can I consider district systems like a "machine" with an COP and EER of 1? For example, If I have this outputs and i want to use a heater of COP 0.8, Can I just multiply the District heating output with 0.8? Thank you.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2019-07-18 10:49:21 -0500

Yes, the DistrictHeating and DistrictCooling objects output total energy transfer, so if you know your district systems annualized COP for heating and cooling you can multiply that by the district output to get total energy use.

edit flag offensive delete link more

Comments

Thank for your answer. All clear.

gonchotorena's avatar gonchotorena  ( 2019-07-18 13:59:06 -0500 )edit