Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

How to connect chilled water loop to PAU coil and Chilled Beam coil in series?

asked 2019-07-07 00:58:14 -0500

katsuya.obara's avatar

updated 2020-01-20 12:03:53 -0500

I want to connect chilled water loop to PAU coil and Chilled Beam coil in series as below.
image description
However, I cannot find a way how to move chilled beam coil in plant loop as shown below.
Can anyone tell me how to do that?
image description

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
4

answered 2019-07-08 09:20:55 -0500

After creating your chilled water coils in each component, you should be able to find the PAU coil under the My Model section of OpenStudio on the right when you are editing HVAC diagrams. Follow these steps to have the two chilled water coils in series:

  • Go to the HVAC Systems tab of OpenStudio and select the chilled water loop (same loop from your screenshot above)
  • Click on My Model near the top right corner
  • Click on Coil Cooling Water (you should see the name of the PAU cooling coil)
  • Drag and drop the PAU cooling coil upstream (to the right) of the chilled beam coil on the demand side of the chilled water loop

When finished, the chilled water loop should look like the screenshot below.

image description

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

3 followers

Stats

Asked: 2019-07-07 00:58:14 -0500

Seen: 327 times

Last updated: Jul 08 '19