Cooling tower out of model boundaries E+

asked 2019-07-02 08:12:01 -0600

Saif's avatar

updated 2019-07-17 07:45:35 -0600

I am using OpenStudio / EnergyPlus to model a residential building that utilize water source heat pumps with cooling tower and boiler, after running the simulation I received warnings related to range temperature and approach temperature being out of the model boundaries and suggesting that it will not impact the cooling tower performance. Since I am not an expert in EnergyPlus I wanted to check the effect of this warning so I plotted the inlet and outlet temperature for the supply side of the loop, I noticed that the inlet and outlet temperatures increase and fluctuate when the outside air wet bulb temperature reaches 66 F as you can see in the first and second screen shot. I am guessing this will impact the energy consumption because the WSHP performance decreases when the loop temperature increases, any Idea how to solve this?

image description

image description

image description

image description

Edit: add picture for different types of cooling towers

image description

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
1

answered 2019-07-11 14:42:17 -0600

Based on the first warning about approach temperature and a search of the source code it appears that this CoolingTower:VariableSpeed specified the "CoolToolsCrossFlow" model type which sets the range for approach at 1.11 - 11.11 C.

Without the full idf to see what else is happening, I would suggest switching to the "YorkCalc" model which sets the approach range to 1.11 - 40.0 C. If that doesn't control well, I would try one of the other cooling tower types, either CoolingTower:SingleSpeed or CoolingTower:TwoSpeed.

edit flag offensive delete link more

Comments

Thank you Michael for the response. I tried using “YorkCalc” but it gave similar results to “CoolToolsCrossFlow” model however using the SinglesSpeed cooling tower as you suggested above showed a really good control over the supply temperature as you can seen in the screen shot I added to the question, but the system design is a variable speed cooling tower, the link for the idf file is here

Saif's avatar Saif  ( 2019-07-17 07:49:42 -0600 )edit
1

I'm stumped. Even doubling the tower size doesn't improve the outlet temperature control. New issue posted. #7464

MJWitte's avatar MJWitte  ( 2019-08-20 12:00:29 -0600 )edit

Thanks for following up.

Saif's avatar Saif  ( 2019-08-21 07:47:32 -0600 )edit