Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

energyplus heating and cooling load

asked 6 years ago

xzb86's avatar

updated 6 years ago

I'm working on FCU + DOAS system, I find that if I increase the outdoor air Volume., the load of FCU coil and DOAS coil will increase simultaneous (component sizing summary). the load has been doubled.

what shall I do if I want to use FCU deal with internal load, while use DOAS to deal with outdoor air load.

thank you

Preview: (hide)

Comments

Do you have an outdoor air flow rate set in your fan coil units?

mdahlhausen's avatar mdahlhausen  ( 6 years ago )

yes, I add the OA flow rate in the HVACTemplate:Zone:FanCoil,, because I'm not sure how to add OA flow rate directly into the HVACTemplate:System:DedicatedOutdoorAir,.

xzb86's avatar xzb86  ( 6 years ago )

1 Answer

Sort by » oldest newest most voted
2

answered 6 years ago

Set the outdoor air flow rate in your fan coil units to zero and then add a DOAS air loop with terminals serving each zone.

Preview: (hide)
link

Comments

ok, I have a DOAS terminal (AirTerminal:SingleDuct:VAV:NoReheat), but how can I set OA to this terminal? I find no OA setting in this air terminal.

xzb86's avatar xzb86  ( 6 years ago )

Set the outdoor air requirement with the DesignSpecificationOutdoorAir object. Alternatively, you can use the AirTerminal:SingleDuct:Uncontrolled object and size the terminal for the outdoor air flow rate directly. Make sure the sizing criteria for the air flow is set to account for the DOAS and sized to air flow requirement.

mdahlhausen's avatar mdahlhausen  ( 6 years ago )