Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

How to set the leaving and entering water temperature of water-to-water heat pump in energyplus

asked 2019-03-05 02:03:05 -0500

l1023's avatar

updated 2019-03-05 03:33:55 -0500

Set the water temperature of water-to-water heat pump

edit retag flag offensive close merge delete

Comments

Could you please retag your question using existing tags and the software you're using? Also a little bit more of context, which object exactly you're using, etc, would help.

Julien Marrec's avatar Julien Marrec  ( 2019-03-05 02:35:42 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
1

answered 2019-03-05 07:33:06 -0500

The leaving water temperature is set in the plant using a SetpointManager:* object. Place a set point manager at the outlet node of the plant. Typically the water temperature is held fairly constant so the SetpointManager:Scheduled object is commonly used. Other managers can be used, for example SetpointManager:OutdoorAirReset. The entering water temperature is the temperature of the water entering the plant (plus possible pump heat) and is a result of the components used on the demand side of the water loop and how those components operate. Control of the return water temperature is not typically used.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2019-03-05 02:03:05 -0500

Seen: 262 times

Last updated: Mar 05 '19