How to set the leaving and entering water temperature of water-to-water heat pump in energyplus

asked 2019-03-05 02:03:05 -0600

l1023's avatar

updated 2019-03-05 03:33:55 -0600

Set the water temperature of water-to-water heat pump

edit retag flag offensive close merge delete

Comments

Could you please retag your question using existing tags and the software you're using? Also a little bit more of context, which object exactly you're using, etc, would help.

Julien Marrec's avatar Julien Marrec  ( 2019-03-05 02:35:42 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
1

answered 2019-03-05 07:33:06 -0600

The leaving water temperature is set in the plant using a SetpointManager:* object. Place a set point manager at the outlet node of the plant. Typically the water temperature is held fairly constant so the SetpointManager:Scheduled object is commonly used. Other managers can be used, for example SetpointManager:OutdoorAirReset. The entering water temperature is the temperature of the water entering the plant (plus possible pump heat) and is a result of the components used on the demand side of the water loop and how those components operate. Control of the return water temperature is not typically used.