How to set the leaving and entering water temperature of water-to-water heat pump in energyplus

asked 6 years ago

l1023's avatar

updated 6 years ago

Set the water temperature of water-to-water heat pump

Preview: (hide)

Comments

Could you please retag your question using existing tags and the software you're using? Also a little bit more of context, which object exactly you're using, etc, would help.

Julien Marrec's avatar Julien Marrec  ( 6 years ago )

1 Answer

Sort by » oldest newest most voted
1

answered 6 years ago

The leaving water temperature is set in the plant using a SetpointManager:* object. Place a set point manager at the outlet node of the plant. Typically the water temperature is held fairly constant so the SetpointManager:Scheduled object is commonly used. Other managers can be used, for example SetpointManager:OutdoorAirReset. The entering water temperature is the temperature of the water entering the plant (plus possible pump heat) and is a result of the components used on the demand side of the water loop and how those components operate. Control of the return water temperature is not typically used.