Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Variable Refrigerant Flow gas-powered auxiliary heat

asked 2019-01-28 16:25:37 -0600

updated 2019-01-28 16:33:29 -0600

I am modeling an air cooled VRF system that is designed to be heated by Gas-fired Heaters when the OA temperature is below 40F. Is there a way for me to change the fuel type of the auxiliary heat?

I looked into changing the fuel type to Gas using an EMS whenever the OAT is below 40F, but it looks like everything in the condenser side would be Gas Powered (including pumps and fans).

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2019-01-29 05:51:13 -0600

Jim Dirkes's avatar

How about DISabling the VRF completely below 40F AND ENabling a separate gas heater system at the same outdoor air temp? VRF is a zone system, so you can use a gas-fired heating system in the same zone (or multiple zones)

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2019-01-28 16:25:37 -0600

Seen: 120 times

Last updated: Jan 29 '19