Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

DOE prototype Midrise Apartment Water heater size

asked 2019-01-24 18:12:22 -0500

Li_Liu's avatar

updated 2019-01-27 09:45:36 -0500

I loaded DOE prototype midrise apartment and I found that it's using 1150 gal electricity water heater, while highrise apartment is using 600 gal natural gas ones. It makes no sense cause midrise apartment has about 32 units and highrise apartment has around 80 units, and end use percentage by water system for midrise apartment is too high.

How can I fix that and is there any standards for that?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2019-01-25 02:49:42 -0500

updated 2019-01-25 02:49:52 -0500

Table 2.2 of Enhancements to ASHRAE Standard 90.1 Prototype Building Models (PNNL 2014) describes the behavior, it represents 23 separate 50 gallon hot water heaters. So while both Hi-Rise and Mid-Rise are modeled as a single water heater, the Mid-Rise water unit is representing a non-centralized system, and as a result has a higher combined storage capacity.

This is also addressed in Appendix A.1.1 (Water Heater Type) and Table A.4. (Total Pipe Thermal Loss For Prototype Buildings) in the same document.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2019-01-24 18:12:22 -0500

Seen: 146 times

Last updated: Jan 25 '19