BCVTB energyPlus+Matlab sizing period simulations not working

asked 2019-01-14 21:42:13 -0600

Divya's avatar

updated 2019-01-15 19:43:20 -0600

Hello, I am using BCVTB to couple MATLAB and energyPlus. I use auto size for HVAC capacity and specified all schedules (Internal heat gains and cooling set points) for a Summer Design day. The run period is for a week long including the summer design day. When I run the idf file from energyPlus, HVAC is able to meet the setpoints for all days. But when I use externalinterface object with ptolemy server (BCVTB) and couple with MATLAB, the HVAC is not able to meet the setpoints. I figured out that the sizing calculations for the design day are not being simulated in the second case. Can someone explain or direct me on how to include the design day sizing simulations using the BCVTB for energyplus. Thanks in advance

edit retag flag offensive close merge delete

Comments

I also realized that when I select Yes for both "Run simulation for sizing periods" and "Run simulation for weather file run periods" and included the design day (6/18) in the run period (6/15 to 6/23), the environment temperatures for the day (6/18) is different in the results for sizing period and run period. It looks strange for me.

Divya's avatar Divya  ( 2019-01-14 21:51:28 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
2

answered 2019-01-15 06:43:21 -0600

There is no data exchange between the BCVTB and EnergyPlus during the sizing and the warm up period, which explains your results. See section 5.3 in https://simulationresearch.lbl.gov/bc...

edit flag offensive delete link more