Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Zone ideal load zone latent cooling/Heating rate

asked 2018-12-12 16:27:04 -0600

marianatonini93's avatar

updated 2018-12-13 14:02:50 -0600

Só I dont understand how E+ calculates the latent loads on an ideal system. I am using a constant supply humidity ratio both for dehumidification and humidification, but can’t connect the latent loads results with the humidity ratio found for the zone. What is the latent load connect with??

edit retag flag offensive close merge delete

Comments

What else is going on in the zone? Infiltration? People? Is the ideal loads system adding outdoor air?

MJWitte's avatar MJWitte  ( 2018-12-14 16:34:56 -0600 )edit

There is infiltration at rate 1/hr and 5 people with an occupation schedule. There is no outdoor air added.

marianatonini93's avatar marianatonini93  ( 2018-12-14 19:01:16 -0600 )edit

1 Answer

Sort by » oldest newest most voted
1

answered 2018-12-20 14:27:57 -0600

The zone humidity ratio is the result of the ideal loads flow (as the specified constant humidity ratio), the latent load from people, and the latent addition or removal due to infiltration. The ideal loads system, when controlled to a constant supply humidity ratio (and with no outdoor air) simply takes the zone return air humidity ratio and lowers (or raises) it to match the specified supply humidity ratio.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2018-12-12 16:27:04 -0600

Seen: 284 times

Last updated: Dec 20 '18