Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Humidifier:Steam:Gas workaround

asked 2018-12-06 10:09:52 -0500

Ruth Urban gravatar image

updated 2018-12-06 13:03:36 -0500

OpenStudio has an electric humidifier but not a gas humidifier, best I can figure out. I see documentation on this: "Humidifier_Steam_GasFields Class Reference." Does that mean that the infrastructure for writing an OpenStudio measure exists, or would I have to write an EnergyPlus model?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2019-03-20 14:35:05 -0500

Ruth Urban gravatar image

Since no one else answered this--I am fairly confident the answer is "no"--I wound up modelling an electric humidifier and then doing a calculation outside of the simulation to approximate a natural gas humidifier.

edit flag offensive delete link more

Comments

1

You're correct.,As of OS 2.7.1 the HumidifierSteamGas class has not been wrapped so that it's available for OpenStudio measures. However, one could write an EnergyPlus Measure to swap instances of HumidifierSteamElectric objects to gas.

An easy way to determine whether a class has been wrapped is to do a search in the SDK Model Docs.

MatthewSteen gravatar imageMatthewSteen ( 2019-03-20 21:41:27 -0500 )edit

Thanks for the suggestion!

Ruth Urban gravatar imageRuth Urban ( 2019-03-25 09:54:09 -0500 )edit