Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
6

Thermal energy storage in Openstudio

asked 2015-03-10 18:06:49 -0600

rkbest's avatar

updated 2015-03-13 15:14:08 -0600

Has anyone implemented TES with HVAC for the building and system model in EP or openstudio. I am trying to get a commercial building modeled with TES and would like some assistance on how can that be achieved. Any thought on how to take care of the control strategy instead of thermal mass where charge and discharge can be scheduled. And how can EP help in sizing that with given variables like hours of operation charge and discharge.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2015-03-11 13:15:18 -0600

The simplest way to do this is probably using water heaters /water tanks. In OpenStudio, you can set up the plant loops in the usual way, and the setpoint manager(s) will provide for an easy control of loop(s). In OpenStudio, you can also use options for auto-sizing instead of hard-sizing for water heaters, pumps, etc.

edit flag offensive delete link more

Comments

According to the IDD the WaterHeater:Mixed object can't have a negative capacity so this workaround would only work for a heat storage scenario not ice storage.

MatthewSteen's avatar MatthewSteen  ( 2015-03-12 22:32:16 -0600 )edit

There are two Ice Storage examples in the EnergyPlus examples file folder, which might help you.

OS-user-AT's avatar OS-user-AT  ( 2015-05-13 15:13:06 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

Stats

Asked: 2015-03-10 18:06:49 -0600

Seen: 1,076 times

Last updated: Mar 11 '15