Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Open studio load calculation

asked 2018-11-12 08:36:31 -0500

Chriskab's avatar

Hello I am training with openstudio. My goal is load calculation with openstudio. I don't know what I am doing wrong but I have no load calculation in my reports. My buiding is a single room with 2 windows. No hvac devices is used. Weather file is form montreal , canada.

Thanks a lot for any help.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2018-11-12 09:26:14 -0500

You need to click the "Enable Ideal Air Loads" checkbox on the Thermal Zones tab for the zones for which you want load to be calculated (and add thermostats schedules for these too)

edit flag offensive delete link more

Comments

I did your suggestion. I still don't have a number on HVAC sizing summary in report. How to set indoor Design temperature maybe this is the key.

Chriskab's avatar Chriskab  ( 2018-11-12 12:14:59 -0500 )edit
1

Indoor design temperatures are controlled by the thermostat schedules that you put for the thermal zones, including their "Design Day" profiles (summer and winter). Also make sure you import design days on the first tab (Load "DDY")

Julien Marrec's avatar Julien Marrec  ( 2018-11-13 02:24:41 -0500 )edit
1

Thanks.. I didn't load DDY. Thanks you for support.

Chriskab's avatar Chriskab  ( 2018-11-13 08:43:44 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2018-11-12 08:36:31 -0500

Seen: 387 times

Last updated: Nov 12 '18