HVACTemplate:System:ConstantVolume minimum outdoor air schedule doesn't work
This is a question about the HVACTemplate:System:ConstantVolume object in EnergyPlus 9.0. I am defining a schedule in the field "Minimum Outdoor Air Schedule Name" of this template, but the simulation results show that the outdoor air is always entering the zone. I have checked the .expidf file and noticed that the schedule I defined is missing in the corresponding "Controller:OutdoorAir" object. If I fill that "Controller:OutdoorAir" with the schedule, I get the results I expected.
Can you please tell me if there is a way to define the outdoor air schedule with this HVAC Template, without editing the expanded file? Thank you!
This issue has been fixed in EnergyPlus v9.1