adiabatic humidification?

asked 2018-10-26 15:13:59 -0500

s_pourm's avatar

updated 2018-10-29 02:48:39 -0500

I am using OS 2.6,

We only have Humidifier:Steam:Electric and we have the Steam:gas under E+, What is the best workaround for adiabatic humidifier??

And I am also wondering what is the difficulty that adiabatic humidifiers have never added to E+, from what I see it's only a psychometric solver that already exists within the Energyplus??

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
4

answered 2018-10-29 12:52:51 -0500

updated 2020-05-27 10:17:03 -0500

It sounds like you want to use the EvaporativeCooler:Direct:ResearchSpecial object in OpenStudio. This object is similar to the EvaporativeCooler:Direct:CelDekPad, which from the documentation,

"... consists of a rigid media evaporative pad, with water recirculated from a reservoir. The evaporative pad provides the area for the adiabatic saturation of the air. While the process provides a lower dry-bulb temperature, the moisture content of the leaving air is higher than the entering condition. The direct stage is used for comfort cooling in a building where adding humidity to the air can be tolerated."

This "research special" evaporative cooler just has a different set of input fields than the "Cel Dek Pad". The "Cel Dek Pad" is not available in the OpenStudio application for v2.6.

UPDATE

After some review with the research special evaporative cooler, it appears that EnergyPlus is currently set up to control outlet temperature of the cooler -- applying a humidity setpoint manager to the evaporative cooler's outlet node has no impact. To get around this, you can apply a temperature setpoint manager to the evaporative cooler's outlet node so that the corresponding outlet humidity provides enough humidification for your needs.

edit flag offensive delete link more

Comments

Any update on this object or any new objects? I wish I could set a humidity setpoint manager.

Keigo's avatar Keigo  ( 2022-08-22 01:15:38 -0500 )edit