Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

How to model constant air volume system using eQUEST?

asked 2018-10-12 09:33:05 -0500

yongqingzhao's avatar

updated 2018-10-15 19:06:51 -0500

How do you model constant air volume system using eQEST? As I know,most of eQUEST users model constant volume system as VAV system but set the minimum airflow setpoint to 1.0.And I think this method is not appropriate,because the VAV system adjusts the cooling and heating load by varying the supply air volume but keep the supply air temperature constant, set the minimum airflow setpoint of VAV system to 1.0 means that the supply air volume and temperature are kept constant,however,the constant air volume system adjusts the heating and cooling load by varying the supply air temperature but keep the supply air volume contstant. I always model the constant air volume as single zone reheat.And I want to kown what your solution to this problem is!

Any suggestion?Thanks!

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
2

answered 2018-10-15 17:53:22 -0500

Erik Kolderup's avatar

You can change the system input for "Cool Control" to have the supply air temperature vary. You probably want to choose "Warmest" as the option instead of "Constant". That will reset the supply air temperature each hour based on zone demand.

image description

edit flag offensive delete link more
1

answered 2018-10-15 22:44:20 -0500

Nick Caton's avatar

So to be clear, you have quite a few options with VAV and with CV system types in eQuest, and a VAV system made to produce CV can still be made to vary supply temperature if that's desired. If you're looking for something like a classification to help you guide which system type options to consider for a given project, I may suggest investing a little time reviewing & absorbing the reference manual entries at and beneat: Volume 1: Basics > Air-side Components > Introduction > Air Systems. There you can find a descriptive/illustrated classification of airside system types. It isn't comprehensive but could help you get the lay of the land.

I wouldn't venture that I really have a favorite per se, however for system types which are natively CV, I probably utilize PTAC, UHT/UVT, PSZ and MZS/PMZS system types most often. It is a little extra work to make a VAV system type behave as though it's contant volume, however that effort can make parametric "VAV conversion" a relatively simple task, and for that reason primarily I and others do often leverage VAVS/PVAVS some fraction of the time where I intend to quantify savings potential for such an ECM.

I hope that's helpful!

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2018-10-12 09:33:05 -0500

Seen: 585 times

Last updated: Oct 15 '18