Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Any way to use biquadratic curve for EIR curve of PLR in Chiller?

asked 2018-10-03 23:30:46 -0500

katsuya.obara's avatar

I am thinking to use excel spreadsheet published by IES to get performance curve regression.
However, this spreadsheet use not only Part Load Ratio but also use temperature difference as below.
On the other hand, Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve expect only Part Load Ratio for variable.
Are there any way to include chiller temperature difference as variable for Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve?
image description

edit retag flag offensive close merge delete

Comments

Julien Marrec's avatar Julien Marrec  ( 2018-10-04 03:56:53 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
4

answered 2018-10-04 20:42:59 -0500

You can't directly use water temp in the performance curve unless the Chiller:Electric:ReformulatedEIR is used. But you could override the curve result and thereby allow any form of performance curve calculation using the Energy Management System (EMS). See EMSCurveOverride_PackagedTerminalHeatPump.idf example file as a template for how to do this.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2018-10-03 23:30:46 -0500

Seen: 470 times

Last updated: Oct 04 '18