Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

No flow through bypass branch, EnergyPlus

asked 2018-10-03 09:33:32 -0500

madisonlikins's avatar

updated 2018-10-03 09:55:32 -0500

I am currently looking at the demand side of a loop that has a heat exchanger and a bypass pipe. I want to use the heat exchanger availability to turn it off for certain hours and have the flow go through the bypass. Right now no flow goes through the bypass and the whole loop is basically turning off when the heat exchanger is off. I have attached a screen shot of my heat exchanger inputs, excluding the availability schedule. The bypass branch is an adiabatic pipe and is correctly attached to the required connectors. Does anyone know why the flow will not go through this bypass branch? Please let me know if any additional information would be useful.

image description

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
0

answered 2018-10-12 07:34:48 -0500

A bypass pipe will never request flow, so the loop pump thinks it should be off when the HX is off. If you use a constant speed pump and set the "Pump Control Type" to Continuous, then there should always be flow through the HX and/or the bypass pipe.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

2 followers

Stats

Asked: 2018-10-03 09:33:32 -0500

Seen: 315 times

Last updated: Oct 12 '18