Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Difference Between Peak and Estimated Sensible Load

asked 2018-09-30 13:44:15 -0500

Siv's avatar

updated 2018-10-01 00:58:12 -0500

Someone please tell me what the Difference Between Peak and Estimated Sensible Load in the facilityloadcomponentsummary is ? what does the two terms mean ?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2018-10-15 16:38:25 -0500

The Zone, Airloop, and Facility component loads summary reports are all structured in a similar way. First there is a large table of "Estimated Cooling/Heating Peak Load Components". Below that is a smaller "Cooling/Heating Peak Conditions" table. The question here asks about these two lines in the Peak Conditions Table

Peak Sensible Load [W]  -13845.7
Estimated Instant + Delayed Sensible Load [W]   -13793.7
Difference Between Peak and Estimated Sensible Load [W] -52.0

The "Peak Sensible Load" is the actual peak load from the zone sizing calculations using the full zone heat balance.

The "Estimated Instant + Delayed Sensible Load" is the equivalent total from the estimated load components table (sum of the first two columns).

"Difference Between Peak and Estimated Sensible Load " indicates how good the component estimates are. The components are estimated in a side calculation which attempts to separate the full peak load into it's various components.

Also see "Component Load Summary" in the Input Output Reference.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2018-09-30 13:44:15 -0500

Seen: 607 times

Last updated: Oct 15 '18