Cooling minimum air flow fraction ?

asked 2018-09-28 00:17:32 -0500

Siv's avatar

updated 2018-10-15 19:10:02 -0500

Will the Sizing:Zone:Cooling Minimum Air Flow Fraction input still be used to set minimum air flow for VAV systems even if my Cooling Design Air Flow Method = DesignDay ?

if yes, what is the ideal value used in the industry ? How to set the minimum air flow fraction value ?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2018-10-04 21:31:29 -0500

The Sizing:Zone, Cooling Minimum Air Flow Fraction input is used in two places as far as I can tell. I doesn't matter which cooling air flow sizing method is used, if this field is entered then it is used here:

DesCoolVolFlowMin = max(DesCoolMinAirFlow,
                                       DesCoolMinAirFlow2,
                                       DesCoolVolFlow * thisTUFZSizing.DesCoolMinAirFlowFrac);

and here:

// set the zone minimum cooling supply air flow rate. This will be used for autosizing VAV terminal unit
// minimum flow rates (comment seems incorrect, really used as a minimum lower limit for the maximum air flow)
FinalZoneSizing(CtrlZoneNum).DesCoolVolFlowMin =
    max(FinalZoneSizing(CtrlZoneNum).DesCoolMinAirFlow,
           FinalZoneSizing(CtrlZoneNum).DesCoolMinAirFlow2,
           FinalZoneSizing(CtrlZoneNum).DesCoolVolFlow * `FinalZoneSizing(CtrlZoneNum).DesCoolMinAirFlowFrac`);

Don't worry too much about what this code does, more importantly that input is used to limit the cooling minimum flow rate during the sizing procedure.

edit flag offensive delete link more