Why do we need 7 design days ?
Whenever I import a DDY file into OpenStudio, I am able to see 7 design days. 4 for summer and 3 for winter. Why do we need 7 design days ? what is the significance of this? Isnt one design day for summer and one for winter sufficient ?
To me that's duplicated from https://unmethours.com/question/17053... see my answer there, I explain the design days and when you need each. If you only have simple equipment, and no cooling towers, you could get away with using only 2 design days. I suggest closing this thread
Thank you, I just have a small doubt, suppose I add cooling towers to my model and cooling is the only objective, should I include
Condns WB=> MDB
in addition toDB=>MWB
or justCondns WB=> MDB
will suffice.Try both, look at your peak cooling and sizing values, and decide for yourself. My advice is that when articulating the model or debugging, it's fine to use only two sizing design days to speed things up. Worst case you just add it in the final run.
Cool...………………...
I personally tend to use both
Condns WB=> MDB
andDB=>MWB
whenever I have cooling towers, regardless or whether I have other cooling eq., but I don't have any hard evidence that it's warranted.