Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Air volume flow rate per watt of rated total cooling capacity is out of range at 6.741E-005 m3/s/W

asked 2018-09-17 03:30:54 -0600

Siv's avatar

updated 2018-09-17 07:14:46 -0600

Hi

The Coil Final Gross Total Capacity is 25799.329 Watts. And the Coil Final Reference Air Volume Flow Rate is 1.038939 m3/s. Dividing 1.038939 by 25799.329 gives 4.02700008E-5. But why does the warning in energyplus say "Air volume flow rate per watt of rated total cooling capacity is out of range at 6.741E-005 m3/s/W"

image description

edit retag flag offensive close merge delete

Comments

Is this a sizing warning, or a warning during the simulation which has a timestamp? If so, look at the timestep output for flow rate and coil load.

MJWitte's avatar MJWitte  ( 2018-09-18 16:33:25 -0600 )edit

Lets say, this is a recurring warning during simulation, I was able to divide the flow rate by capacity and equate it. However, could you please tell me how to overcome this issue ? What is the solution to this problem ?

Siv's avatar Siv  ( 2018-09-18 22:54:33 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
0

answered 2018-09-19 05:56:11 -0600

Siv's avatar

I was able to resolve this error by using the setpoint manager "Setpoint Manager Single Zone One Stage Cooling" previously I was using "Setpoint Manager Single Zone Cooling" Could someone explain why this is happening ?

edit flag offensive delete link more

Comments

We need to know more about the rest of the HVAC system in order to help. What kind of air terminal units, airloohvac components, etc. Or just post the full idf.

MJWitte's avatar MJWitte  ( 2018-09-19 10:09:16 -0600 )edit

I have used "Setpoint Manager Single Zone Cooling" for Thermal Zone 1 and "Setpoint Manager Single Zone One Stage Cooling" for Thermal Zones 2, 3 and 4. The Warning regarding "Air volume flow rate per watt of rated total cooling capacity"occurs only for the COIL COOLING DX SINGLE SPEED 1 which serves Thermal Zone 1. Kindly help me why this occurs and I have added a link to my model as well as the climate file.

https://drive.google.com/open?id=1x9r...

Siv's avatar Siv  ( 2018-09-19 23:20:21 -0600 )edit

These warnings can be overly protective at times. The warnings use the System Node Current Density Volume Flow rate divided by the rated capacity. So, the value will vary as the inlet conditions change. This model has just a few warnings and the max value is only slightly above the range. I would just ignore the warnings

MJWitte's avatar MJWitte  ( 2018-09-25 13:54:47 -0600 )edit

I understand, however how does the warning not appear when I change the setpoint manager to "Setpoint Manager Single Zone One Stage Cooling" ?? this is what is confounding me

Siv's avatar Siv  ( 2018-09-27 04:51:26 -0600 )edit

That's a difficult question to answer without running both cases in debug mode to check values. Based on a check of the source code, the air volume flow rate for this warning is calculated from the mass flow rate using the density at coil entering conditions. These conditions will change with the two different setpoint managers. I wouldn't be concerned about these warnings.

MJWitte's avatar MJWitte  ( 2018-10-04 14:42:43 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2018-09-17 03:30:54 -0600

Seen: 825 times

Last updated: Sep 19 '18