setCondenserType not working for "WaterCooled" - defaults back to "AirCooled"

asked 2018-09-12 16:31:49 -0600

su2zafar's avatar

updated 2018-09-24 11:42:14 -0600

I'm trying to add a Water Cooled Chiller to a prototypical building. I downloaded the "AedgOfficeHvacVavChW" measure from BCL and tweaked it a little bit to be used for different HVAC systems depending on user input. In case the user input is "Water Cooled Chiller", the setcondenserType command doesn't work for "WaterCooled" and whenever you try to set it to "WaterCooled", it defaults back to "AirCooled". Has anyone else faced the same issue or knows whats going on here? It works perfectly fine when you're changing the condenser to "EvaporativelyCooled".

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2018-09-12 23:02:26 -0600

My cursory look at the OpenStudio source code suggests that the chiller needs to be connected to a secondary PlantLoop before setting the condenser type to WaterCooled.

edit flag offensive delete link more

Comments

Thanks for the comment. So, I have to make the condenser (secondary) loop first and then set the condenser type to WaterCooled?

su2zafar's avatar su2zafar  ( 2018-09-13 09:39:28 -0600 )edit

Here's an example of it being used.

shorowit's avatar shorowit  ( 2019-04-27 07:31:13 -0600 )edit