Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
9

Obtaining Chiller Data from Manufacturers

asked 2018-09-03 20:13:02 -0500

updated 2018-09-04 08:49:03 -0500

Does anyone have suggestions, tips, or tricks to more easily obtain chiller data from manufacturers representatives? I haven't had too much trouble getting part load data, but for full load data it seems to be impossible. I am specifically working with Daikin.

I have tried using the Taylor Engineering Chiller bid form, but the reps still claim that their chillers have the same capacity no matter what the chilled water and condenser water conditions are. I've even looked at their selection software inputs and outputs, and capacity is always an input, there is no way to output capacity at full load to see how it changes with temperature.

C:\fakepath\DaikinSelectionSoftware.png

Has anyone else run into this issue?

edit retag flag offensive close merge delete

Comments

1

I just got the data from a JCI/York rep! The first person at any chiller manufacturer to actually find it and give me what I need.

bbrannon4's avatar bbrannon4  ( 2018-09-06 04:17:37 -0500 )edit
1

This is interesting because I have successfully gotten Daikin, Trane, and York to fill out the Taylor Chiller bid form. Makes me wonder if they faked some of the numbers to fill out the form. I have not had success using the new one IES created. There seems to be a bug somewhere.

crduggin's avatar crduggin  ( 2018-09-10 16:59:50 -0500 )edit

These seem to answer my question... the answer is, yes, I'm not crazy and the manufacturers should have this data. So keep trying. Thanks @crduggin and @bbrannon4. Post your comments as an answer, please!

Anna Osborne Brannon's avatar Anna Osborne Brannon  ( 2018-09-14 01:15:44 -0500 )edit

Done. I can provide a good contact for getting Daikin chiller performance if you are interested.

crduggin's avatar crduggin  ( 2018-09-15 12:05:24 -0500 )edit

Thanks for the great question, Anna. We are constantly running into this issue as well. Just wanted to update the Taylor bid form link, as the original link is broken.

Updated Bid Form Link

codybond's avatar codybond  ( 2022-04-23 12:17:16 -0500 )edit

2 Answers

Sort by » oldest newest most voted
2

answered 2018-09-15 12:04:19 -0500

crduggin's avatar

This is interesting because I have successfully gotten Daikin, Trane, and York to fill out the Taylor Chiller bid form. Makes me wonder if they faked some of the numbers to fill out the form. I have not had success using the new one IES created. There seems to be a bug somewhere.

edit flag offensive delete link more

Comments

Thanks! I think the issue is that representatives in Australia may not be as used to providing this data as they are in the US. If you can send me your US contacts, I’ll try to see if they can send me the data.

Anna Osborne Brannon's avatar Anna Osborne Brannon  ( 2018-09-15 18:17:41 -0500 )edit
4

answered 2018-09-07 14:25:45 -0500

Brett M's avatar

"Full-load", "Load" and "Part-load" can be a confusing when referring to chillers as the term gets used for evaporator cooling load, condenser heat rejection load and compressor load (aka input power).

What we really want to know is the evaporator load (aka "capacity" or the evaporator flow rate and water delta T) at a fixed compressor load (compressor at 60 Hz or full speed) while holding flow constant (as you have shown in the selection software screenshot).

Most of the manufacturers representative's selection software is not set-up well to output this information as they very rarely would want to run a compressor full speed at low lift conditions if they can avoid it. In practice, running a compressor at full speed during low lift conditions can cause instability in the chiller operation and as a result the manufacturer may limit selections at those conditions or not have useful test data (hence note #2 in the bid form about stable operation). The compressor loading is primarily a function of lift (approximately by leaving condenser and evaporator temperatures) to manage refrigerant pressure in the evaporator and condenser while the output capacity (evaporator cooling load) is primarily a function of refrigerant mass flow rate. In a centrifugal chiller with a variable speed compressor the refrigerant flow is typically controlled by inlet guide vanes mostly independent of the compressor. As a result, in modern centrifugal chillers the available evaporator capacity may change very little across varying lift conditions because the inlet guide vanes may be limiting the refrigerant mass flow by design to keep the compressor lift low (and reduce speed/power consumption) although the exact control may vary based on manufacturer. Some manufacturers have an easier time producing this information particularly if the run low pressure machines that are more tolerant of a wider range of low lift operating conditions (like York and Trane centrifugal machines currently do).

The chiller EIR model curves do not capture a lot of these intricacies of modern chillers very well particularly for machines with multiple compressors or variable speed compressors. For single-compressor constant speed machines this data is much more straight-forward to test for and build a model around.

You may try asking for the selection at a constant input power at the various leaving condenser and evaporator water temperatures and then calculate the resulting capacity from the evaporator temperature differential. This can result in a lot of guess and check selections that the sales representative may not want to perform. The factory may have that information more readily available even if not officially published in the selection software for their representatives.

edit flag offensive delete link more

Comments

I just the information from a Daikin representative in US. I confirmed Trane can get this information from their selection software TOPPS in the form of an XML export.

Brett M's avatar Brett M  ( 2018-09-14 12:34:01 -0500 )edit

Thank you! I think the issue might be that I am in Australia and the representatives here use different software than in the US? I tried to reach out to a couple of reps in the US but haven’t had success yet.

Anna Osborne Brannon's avatar Anna Osborne Brannon  ( 2018-09-15 18:17:05 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

2 followers

Stats

Asked: 2018-09-03 20:13:02 -0500

Seen: 1,046 times

Last updated: Sep 15 '18