what is the exact values to be inputted in Cooling Coil DX Single Speed?

asked 2018-08-27 21:56:08 -0500

Philip Caesar Ebit's avatar

updated 2018-08-28 09:50:29 -0500

I am doing an EnergyPlus simulation using the actual air-conditioning units of the building. The ACU's are window type therefore, I used the ZoneHVAC:WindowAirConditioner of the IDF and that also needs the data of the cooling coil to used. Now, I used the Cooling Coil DX Single Speed and I find it difficult on what values be inputted in the following: 1. Gross Rated Cooling Capacity 2. Gross Rated Heat Sensible Ratio 3. Rated Air Flow Rate

I would like to ask a help on how to solve this values or are there any constants to multiplied since I modeled an actual 2.5 horsepower ACU.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2018-08-31 20:03:15 -0500

Look up the data on the manufacturers site. Your AC unit has a model number, google that number and look up the specifications. Manufacturers data will include the data your looking for, total rated capacity, SHR (or they show total and sensible capacity where SHR = sensible/total), and air flow rate. Look for the data at 35 C (95 F) outdoor dry-bulb temperature and 19.44 C (67 F) indoor wet-bulb temperature and use that data to input your HVAC unit.

edit flag offensive delete link more

Comments

okay Sir Richard, thank you for these information.

Philip Caesar Ebit's avatar Philip Caesar Ebit  ( 2018-09-03 20:30:37 -0500 )edit