monthly results Data viewer

asked 2018-08-15 10:44:47 -0500

youssra's avatar

In the results I found that my building needs cooling throughout the year (even in winter) at the same time it needs heating in winter. can the building need heating and cooling at the same time?

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
2

answered 2018-08-15 11:35:39 -0500

Yes, you can have a core zone that needs cooling year round while perimeter zones are in heating.

edit flag offensive delete link more

Comments

In general yes, but not in BEopt.

shorowit's avatar shorowit  ( 2018-08-15 19:18:48 -0500 )edit

thanks; didn't realize this was BEopt specific

mdahlhausen's avatar mdahlhausen  ( 2018-08-15 21:32:55 -0500 )edit

Agreed that it wasn't super obvious, but he/she did use the beopt tag.

shorowit's avatar shorowit  ( 2018-08-15 21:46:13 -0500 )edit
2

answered 2018-08-15 12:05:07 -0500

There can be both heating and cooling within a given month for swing seasons, but you cannot have both heating and cooling at the same time (e.g., for a given hour). For residential buildings, only the heating or cooling system will run at any time.