Have the output "zone total internal latent gain energy"

asked 2018-08-09 22:24:17 -0500

Alexis's avatar

updated 2018-08-10 07:51:54 -0500

Hello I have run my energy plus simulation, so I have the cooling capacity per month so perfect but I would like to have the "zone total internal latent gain energy" image description

For the moment, I have 0. Its weird because I set the number of people/lights

What I need to do ? Thank you

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
0

answered 2018-08-10 09:59:13 -0500

If you have added People objects to zones, then you will want to double-check your input fields for how occupants exchange heat into the zone:

  • Sensible Heat Fraction - Defines split of sensible vs latent heat gain into zone from people. Can be set to constant value by user, or change according to the following activity level schedule input. If you see no latent gains, check if this input is set to 0.
  • Activity Level Schedule Name - Sets the total $W / person$ heat gain into zone. The following table below this documentation section gives typical $W / person$ values for different activities from ASHRAE 2005 Handbook of Fundamentals.

image description image description image description

If you see no latent gains, check if either or both of these inputs is set to 0. If those are both >0, then something else is wrong. In that case, you may have set your occupancy schedule input field to a schedule that's always 0 (people are never in the zone, so they never add heat to the zone).

edit flag offensive delete link more