Increased WWR = Decreased Peak Tonnage?

asked 2018-07-31 12:53:25 -0500

updated 2018-08-06 08:08:58 -0500

Generated the below Sefaira response curve for window-wall ratio versus peak cooling coil load (tons), in yellow and Annual electricity consumption (kWh) in red...

The linear increase in annual energy I get... But the weird cooling coil response curve, I’m having trouble wrapping my head around. Thoughts?

Weird Response Curve

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
1

answered 2018-08-02 10:46:55 -0500

what kind of space use type & interior loads do you have in the model? If heavily interior loaded the heat can get trapped inside and the higher WWR ratio (with u-values which are worse than walls, typ) allows that heat to escape. Would/can also shift when the peak load is occurring since it could be a mix of interior/envelope loads too.

edit flag offensive delete link more

Comments

Ooh, good point. This does have pretty significant internal loads modeled currently... 1.5 W/sf, for a total energy end use contribution on the order of 40%. I like this explanation!

sgudeman's avatar sgudeman  ( 2018-08-02 15:05:25 -0500 )edit