How to get the Cooling Tower Outdoor Air Inlet Node via EMS

asked 2018-06-24 01:58:13 -0600

Fustrated's avatar

updated 2018-06-25 16:31:50 -0600

Hello all, I am trying to modify the outdoor air inlet of a coolign tower, but I do not seem to find the variable anywhere. Only the AHU outdoor air inlet is in the OutdoorAir:NodeList. The help file states that "If this field is left blank, the outdoor air conditions entering the cooling tower are taken directly from the weather data", hence the weather data is employed as the outdoor air inlet, but this does not solve my problem because I only want to modify the outdoor air inlet of the coolign tower (and not the weather data). Any suggestion will be greatly appreciated, I am getting very fustrated. Thanks!

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2018-06-26 19:39:01 -0600

JasperRiikonen's avatar

In the IDF editor you can assign a Node Name to the Outdoor Air Inlet Node Name for the CoolingTower object (e.g. assign it as Air Loop 1|OAD-1 AirSupply InletNode). Then you can use EMS to actuate that node/component.

edit flag offensive delete link more

Comments

In ZoneCoolTower:Shower there is no Outdoor Air Inlet Node and I must change the outdoor air quality that is used by ZoneCoolTower:Shower . What must I do in this case?

taher.ahel's avatar taher.ahel  ( 2018-08-17 10:00:47 -0600 )edit