Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Why does Controller:OutdoorAir not set OA-Flow to zero as specified ?

asked 2018-06-20 02:54:13 -0600

updated 2018-06-20 07:58:06 -0600

I have a simple airloop as shown below:

image description

If Outdoor DB Temperatures are too low, then the Outdoor Air Flow should be set to zero. Accordingly the minimum OA Flow rate has been set to 0 m³/s. See here:

image description

Nevertheless, in the following chart you see that outdoor air flow at the outdoor air IN node never reaches zero, but apparently reaches a minimum greater than zero, the origin of which is totally unclear: image description

Can anyone explain what the reasons might be and how to enforce zero outdoor air flow when outdoor air is too cold ?

edit retag flag offensive close merge delete

Comments

In the AirTerminal:SingleDuct:VAV:NoReheat object - do you have the box "Control for Outdoor Air" checked?

mdahlhausen's avatar mdahlhausen  ( 2018-06-20 12:11:27 -0600 )edit

Is there a zone exhaust fan?

MJWitte's avatar MJWitte  ( 2018-06-20 16:10:11 -0600 )edit

the entries for the VAV object are:

AirTerminal:SingleDuct:VAV:NoReheat

Name =                      Main Zone VAV Air
Availability Schedule Name =System Availability Schedule
Air Outlet Node Name =      Main Zone Inlet Node
Air Inlet Node Name =       Main Zone ATU In Node
Maximum Air Flow Rate =     9
Zone Minimum Air Flow Input Method= Constant
Constant Minimum Air Flow Fraction= 0.05
Fixed Minimum Air Flow Rate = 0
Minimum Air Flow Fraction Schedule Name =
Design Specification Outdoor Air Object Name =

-- There is only a Var Speed Fan in the airloop.

OS-user-AT's avatar OS-user-AT  ( 2018-06-21 02:21:34 -0600 )edit

It's going to be impossible to answer this without seeing the complete EnergyPlus idf file. Please post a link here or e-mail to energyplus-support@gard.ocm

MJWitte's avatar MJWitte  ( 2018-06-21 17:38:16 -0600 )edit

OK, here is a temporary download link

OS-user-AT's avatar OS-user-AT  ( 2018-06-26 05:33:16 -0600 )edit

3 Answers

Sort by » oldest newest most voted
3

answered 2018-06-27 14:53:05 -0600

The Controller:OutdoorAir references a Controller:MechanicalVentilation object which is always on which references a DesignSpecification:OutdoorAir with OA/person (but this zone has no people) and OA/zone = 9 m3/s. (I should have noticed the Mechanical Ventilation Controller name in the screen shot above.)

In general, the outdoor air flow rate will be the greater of the Controller:Outdoorair Minimum Outdoor Airflow Rate (times Minimum Outdoor Air Schedule) OR the flow requested by Controller:MechanicalVentilation (when it's schedule is active). The schedule in DesignSpecification:OutdoorAir is also applied to any values coming from there which feed into the Controller:MechanicalVentilation. Then add in the economizer and other limits for final OA flow rate. See list of limit checks in order in the Input Output Reference in the introduction to Controller:OutdoorAir.

From this input file, the relevant inputs are:

Controller:OutdoorAir,
Outdoor Air Controller,  !- Name
<snip>
0,                       !- Minimum Outdoor Air Flow Rate {m3/s}
Autosize,                !- Maximum Outdoor Air Flow Rate {m3/s}
<snip>
Always Off Discrete,     !- Minimum Outdoor Air Schedule Name
Always Off Discrete,     !- Minimum Fraction of Outdoor Air Schedule Name
Always On Discrete,      !- Maximum Fraction of Outdoor Air Schedule Name
Controller Mechanical Ventilation 1,  !- Mechanical Ventilation Controller Name

Controller:MechanicalVentilation,
Controller Mechanical Ventilation 1,  !- Name
Always On Discrete,      !- Availability Schedule Name
No,                      !- Demand Controlled Ventilation
ZoneSum,                 !- System Outdoor Air Method
1,                       !- Zone Maximum Outdoor Air Fraction {dimensionless}
Main Zone,               !- Zone 1 Name
OA_Design_Zone,          !- Design Specification Outdoor Air Object Name 1
DataCenter Design Air Dist;  !- Design Specification Zone Air Distribution Object Name 1

DesignSpecification:OutdoorAir,
OA_Design_Zone,          !- Name
Flow/Zone,               !- Outdoor Air Method
0.00,                 !- Outdoor Air Flow per Person {m3/s-person}
,                        !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
9,                       !- Outdoor Air Flow per Zone {m3/s}
,                        !- Outdoor Air Flow Air Changes per Hour {1/hr}
Always On Discrete;      !- Outdoor Air Schedule Name
edit flag offensive delete link more
1

answered 2018-06-21 03:35:27 -0600

A solution that works is as follows:

Add a Maximum Outdoor Air Fraction Schedule to Controller:OutdoorAir which is EMS-controlled (in EMS the condition is defined for setting outdoor air flow to zero). Although this works, this solution is not fully satisfactory because it remains unexplained why EnergyPlus produced a minimum outdoor air flow greater than zero in the first place.

edit flag offensive delete link more
0

answered 2020-06-27 03:59:54 -0600

Current economizers cannot provide zero outdoor airflow when the damper is closed, and economizers cannot provide 100% outdoor airflow when the damper is fully open due to uncontrolled damper leakage and perimeter gap leakage. Typical closed economizer damper outdoor airflow without sealed perimeter gap is 10 to 25% and maximum outdoor airflow is 55 to 80%. If the perimeter gap is sealed per US Patent 9,671,125 or patents pending, then the uncontrolled perimeter gap leakage will be 5 to 10% due to damper leakage. Low leakage dampers will have lower leakage, but cannot prevent perimeter gap leakage. Most economizer controllers cannot provide the required minimum outdoor airflow per ASHRAE 62.1 due to economizer actuators not being calibrated per US 10,001,289 and patents pending.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2018-06-20 02:54:13 -0600

Seen: 626 times

Last updated: Jun 27 '18